boat A/C trips breaker

Post by Sean B »

I have a Bertram factory original 1987 era CruiseAir/Dometic split system A/C.

I know just enough about air conditioners to be dangerous, so here is my question. Recently mine will trip the breaker every time the compressor is triggered to come on. The fans run, the water pump runs, the compressor tries to go for half a second, then CLICK.

My first instinct is to replace both capacitors, run and start, and the relay too. I know I probably only need the start capacitor, but I figure while I'm in that little box, I'll freshen them all up.

Sound like the right thing?
Or should I go try whacking the compressor with a hammer first?
(not necessarily a joke, I have heard of this working)
Navatech

Re: boat A/C trips breaker

Post by Navatech »

Sean B wrote:My first instinct is to replace both capacitors, run and start, and the relay too. I know I probably only need the start capacitor, but I figure while I'm in that little box, I'll freshen them all up.
"Use the Force, Luke"... It's pretty basic as well as pretty cheap to follow your first instinct... Even if your compressor will start with a little "love poke" that would be a sign that it's going to die pretty soon...
User avatar
Sean B
Senior Member
Posts: 411
Joined: Jun 30th, '06, 08:03
Location: Melbourne, Florida

Re: boat A/C trips breaker

Post by Sean B »

Thanks... what I'm really interested in is whether those in the know think that I'm wasting (or not wasting) my time swapping out components on a 27 year-old boat A/C system, trying to get the old contraption moving again
RAWicklund
Senior Member
Posts: 159
Joined: Oct 5th, '10, 07:58
Location: Houma, La

Re: boat A/C trips breaker

Post by RAWicklund »

Sean, there are various ways to free a stuck compressor. Hard start kit, reversing motor, hi voltage surge and that big hammer thing. Since your breaker is tripping before the over current protection on the compressor trips.... Your breaker may be a problem also.

The cheapest way for me would be to test caps then put hard start cap in. Once it frees up then put in new capacitors..... I would leave the relay alone only due to higher cost and I've rarely seen them fail when used on ice machines and small refrigeration units..... That might be different for a marine environment .... I've only worked on a half dozen marine AC's.

Not sure what it is with today's capacitors...... Their lifespan is a fraction of their older relatives....cheap manufacturing I guess...but all brands are the same.

Good luck

Ray
1971 Sportfish 314 49 1103
1994 B28 BERF2720L394
User avatar
Charlie J
Senior Member
Posts: 2207
Joined: Jun 29th, '06, 09:14
Location: freeport n.y

Re: boat A/C trips breaker

Post by Charlie J »

I was going to say the breaker could be on its way out
1968 hull # 316 - 757
User avatar
Sean B
Senior Member
Posts: 411
Joined: Jun 30th, '06, 08:03
Location: Melbourne, Florida

Re: boat A/C trips breaker

Post by Sean B »

Hmm I hadn't thought of the breaker. I think I will try that first.

Thank you gentlemen. The formidable b31 board strikes again !
Navatech

Re: boat A/C trips breaker

Post by Navatech »

Sean B wrote:what I'm really interested in is whether those in the know think that I'm wasting (or not wasting) my time swapping out components on a 27 year-old boat A/C system, trying to get the old contraption moving again
Refrigeration units are really quite simple... Not that many moving parts... It's usually something electrical that goes bad... The one reason why compressors don't get replaced that much today is that the appliances are so cheap new out of the box that once you have added up the cost of labor, parts and material you're pretty close to the price of a new unit... Of course, the "marine" units are more expensive so replacing a compressor might still be a viable option...

Having said that, and considering that your unit is 27 year old your biggest issue in trying to replace just the compressor would be finding a suitable compressor (due to lubrication issues compressors are matched to specific refrigerants) and recharging the system with refrigerant... Back then everybody used some type of "Freon" (R-11, R-12 etc)... However, due to ozone depletion potential and global warming potential these earlier refrigerants were phased out... Considering this is the case you might have to purchase a complete unit just because you'll be unable to find the older stuff...
User avatar
Keith Poe
Senior Member
Posts: 491
Joined: Aug 15th, '12, 01:10
Location: Torrance California

Re: boat A/C trips breaker

Post by Keith Poe »

Swap the breaker with another one or swap the wires.

Turn the breaker off and move the motor by hands see if it's tight.

Guy I rebuilt a 250 ton chiller with lost his fingers to a carrier unit they put them back on with limited use.


Image
Sportsmen Conservation Sustainable Harvest Accountability Integrity with the spirit of a Warrior.